I will be installing a feeder for two identical roof top air conditioners. I obtained some data for the A/Cs from a salesman. It was not quite a nameplate, but it's useful. I want to make sure I'm properly crunching the numbers.
The data sheet lists minimum current amps (MCA) and Maximum Overcurrent Protection. I needed the rated load current (RLC). I worked backwards from the MCA to get the RLC.
EG. At 208 volts, 3P, the MCA is 145.5 amps. The maximum overcurrent protection (MOCP) is 250. Here's my math:
(MCA) 145.5 amps - 8 amp fan load= 138.5. 138.5/1.25=110 amps (RLC). The MOCP doesn't work out for that number.
The feeder for the two units would be 110X125% + 8(fans)= 145.5 (amps) + 110 (RLC) + 8 (fans)= 263 amps. Voltage drop will be calculated later.
Expressed another way: 1st unit 145.5amps
2nd unit 110 amps
fans 8 amps
total 263 amps
The feeder would be fused at 350 amps. (MOCP) 250 + 118 (RLC + fans) =368. Next size fuse down 350 amps.
MOCP 1st unit 250 amps
2nd unit RLC + fans 118 amps
total 368 amps
Let me know what you think of my math.
Jim
The data sheet lists minimum current amps (MCA) and Maximum Overcurrent Protection. I needed the rated load current (RLC). I worked backwards from the MCA to get the RLC.
EG. At 208 volts, 3P, the MCA is 145.5 amps. The maximum overcurrent protection (MOCP) is 250. Here's my math:
(MCA) 145.5 amps - 8 amp fan load= 138.5. 138.5/1.25=110 amps (RLC). The MOCP doesn't work out for that number.
The feeder for the two units would be 110X125% + 8(fans)= 145.5 (amps) + 110 (RLC) + 8 (fans)= 263 amps. Voltage drop will be calculated later.
Expressed another way: 1st unit 145.5amps
2nd unit 110 amps
fans 8 amps
total 263 amps
The feeder would be fused at 350 amps. (MOCP) 250 + 118 (RLC + fans) =368. Next size fuse down 350 amps.
MOCP 1st unit 250 amps
2nd unit RLC + fans 118 amps
total 368 amps
Let me know what you think of my math.
Jim