So I say
No
No
No
I would to also add serbice rated ats controller
No
No
No
I would to also add serbice rated ats controller
As Tom suggested, I would not make any decision without consulting NFPA20.
The jockey pump is allowed to be fed by the fire pump service although the ones I have seen were on the building service.
695.4(A) might play a part concerning the "direct connection to the fire pump controller"
An additional service is allowed up to 6 disconnects but the mechanics of adding one while conmpying with 695.4 wouod be trick IMO.
I say it not a jockey pump since a jockey pump is not related to normal water supply. The jockey pump maintains ( maintenance/ maintain pump) pressure on the fire (sprinkler)systems to prevent false alarms.
Let's say they have a roof tank and use this for gravity feed normal water supply and fire suppression. This would be normal water supply and fire protection. This would be the water pump feeding this system. Then exception would apply.
This pump would be allowed to be remote and would count as one of the six handles.
Unless it is locally required to be on alternate power, in which case it must be remote.Jockey pump is not related to normal water supply??
If thats true then service rated controller jockey pump post #1 need to be grouped with switchboard
Where a jockey pump is not required to on any of the alternate power systems, the disconnect is not required to be remote. (See answer to your other jockey pump question.)
Local codes may have different rules than NFPA 20 or NFPA 101.
"The main service controller is located remote from swbds service."
?
Did you mean fire pump controller, jockey pump controller or both.
Going reread nfpa 20 and applicable NEC
I understand what your asking now.
Where in the NEC is this allowed to have both according to the drawing.
The wire way tap to both.
Instead having a proper sized service rated disc than to controllers or an ATS controller via tap.
Is that it ?
Yep understand clearly now
The only problem I would have with it as drawn is, to me, a grey area and that is what I mentioned in Post #19:
695.4(A) Direct Connection. The supply conductors shall directly connect the power source to a listed fire pump controller, a listed combination fire pump controller and power transfer switch, or a listed fire pump power transfer switch.
Depending on how you made your tap to the jockey pump in the wireway would you possibly violate the "direct connection" ? By using a split bolt I;d see no problem, a polaris connector where you actually cut the conductor would be questionable to me but that's a field decision not one with which plans review should be concerned.