I have no back up generator and jockey pump is fed from downstream panelboard. The jockey pump connects to 20A receptacle 120V. Can sprinkler jockey pump be fed from downstream panelboard feeder breaker?
 

JGinIndy

Senior Member
Location
Indiana
Occupation
Retired Electrician currently County Inspector
NEC 695.1(B) does not cover Jockey / Pressure Maintenance Pumps and I don’t have a NFPA 20 handy but if memory serves it’s not required to provide one. Anyway, I don’t see an issue feeding from from the panelboard. I am retired so I may need some dust blown out.
 