Joints in panel

Status
Not open for further replies.

storeytime

Member
Location
Texas
I am finishing a residential job that someone else started. (Nightmare!) The panel is an outdoor, surface mount, 200 amp, 20 space panel. Because of the number of 240V circuits (8), there is not enough spaces to accommodate all the homeruns. I am going to have to install a sub-panel. This will make the homeruns going to the sub panel too short. Can you legally make joints in main panel. Otherwise, I'm going to have to take down the whole service, install a gutter and start over?
 
Yes, splices are permitted.

See 312.8.

Whethere 312.8 actually applies at all has been subject to debate. Either way, the splices are fine.
 
Re: Joints in panel

storeytime said:
Can you legally make joints in main panel.
In my state, it is legal, provided you have a special license. Although, on occasion, the ATF will kick a door down on a cancer patient with a license.

sniperer.gif
deadat30.gif
 
Story, if tandem breakers still won't do it, I'd consider replacing the panel anyway, rather than subbing. Using the same brand of panel would minimize new breaker costs.
 
iwire said:
Jim W in Tampa said:
Not with me but what he would be doing is using the first panel as a raceway.With or without splice it isn't legal

Again I ask for a code section.

I'm with Bob-o here....we need more than a "I say so - so it is" response.
 
Jim W in Tampa said:
Will get the friday for you.

OK I will be holding my breath, is Friday when your photocopied 2005 NEC arrives? :lol: :wink:


Jim W in Tampa said:
Are you saying we can use main panel as a raceway to get to another panel ?

Yes.


Jim W in Tampa said:
I dont think that will fly

It won't fly, the wires hold it down :p but it will pass inspection if they use the NEC. 8)
 
Jim W in Tampa said:
Not with me but what he would be doing is using the first panel as a raceway.With or without splice it isn't legal
But it is. There are even cross-section-area fill limitations.

Added: If memory serves, it's 40% for conductors, and 70% at joints/splices.
 