- Location
- Massachusetts
celtic said:You're brutal...LOL
:lol:
Some of my coworkers would agree and I consider them my friends. :lol:
celtic said:You're brutal...LOL
iwire said:celtic said:You're brutal...LOL
:lol:
Some of my coworkers would agree and I consider them my friends. :lol:
celtic said:iwire said:celtic said:You're brutal...LOL
:lol:
Some of my coworkers would agree and I consider them my friends. :lol:
I didn't say/suggest that you were wrong/out of line...just brutal..LOL.
312.8 Enclosures for Switches or Overcurrent Devices
Enclosures for switches or overcurrent devices shall not be used as junction boxes, auxiliary gutters, or raceways for conductors feeding through or tapping off to other switches or overcurrent devices, unless adequate space for this purpose is provided. The conductors shall not fill the wiring space at any cross section to more than 40 percent of the cross-sectional area of the space, and the conductors, splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space.