Journeymen exam question
FrenchyTech
Maine
Hello! I am preparing for my journeysman exam which I am taking soon and I purchased Mike holts examination preparation course and I came across something that gave me a hard time and I’ll post the question below:
c) 10 AWG
440.33
Conductor Ampacity = (25A × 125%) + 2A
Conductor Ampacity = 31.25A + 2A
Conductor Ampacity = 33.25A
Conductor Size = 10 AWG, rated 30A at 60°C, 110.14(C)(1)(a)(2) and Table 310.16
What I don’t get is why is the conductor a parity above the ampacity of 10 awg? I thought the ampacity always had to be bigger than the calculated amps. Thanks for your time and knowledge!
That sounds like it is your calculation is that correct? Did the question specify terminal temperature ratings? #10 AWG @ 75° C is good for 35 amps.
Was the question about 60C conductor because that is incorrect. If the #10 was 75C then that would be okay because 240.4 (D) & (G) allows #10 to be more than 30 amps for motors.
It would be good to see the question
Sure here’s the question!: What size minimum branch circuit conductor is required for a 25A refrigerant motor compressor with a 2A fan, terminals rated 75 C: A 15 AWG, B 12 AWG, C 10 AWG, and D 8 AWG, I think what’s more getting me is on the answer it said 10 AWG 60 Celsius but that’s 30 Amps but Kayden since the terminal is 75 I can pick from the 75 degree column
It did! It said 75 degree terminals and if that’s what I use to pick the wire ampacity then that makes sense
Yes so since it's a motor compressor with 75° C terminals you can ignore the 30 amp limit for #10 AWG conductors in 240.4 and use the 75° C ampacity of 35 amps from the table.
... I thought the ampacity always had to be bigger than the calculated amps. Thanks for your time and knowledge!
Yep, and the ampacity of #10 copper AWG with 75C terminals is 35 amps, which is larger than the calculated amps of 33.25.
I am guessing what is throwing you off is the requirement of 2020 NEC 240.4 (D) (7), which is about the overcurrent protection of #10 copper being limited to 30 amps. But 240.3 references table 240.3 which references 440 for Air-conditioning and refrigerating equipment.
Article 440 Part VI "Motor-Compressor and Branch-Circuit Overload Protection" is where to look for the breaker size. BUT that is not part of the question. ;)