Hello! I am preparing for my journeysman exam which I am taking soon and I purchased Mike holts examination preparation course and I came across something that gave me a hard time and I’ll post the question below:
c) 10 AWG
440.33
Conductor Ampacity = (25A × 125%) + 2A
Conductor Ampacity = 31.25A + 2A
Conductor Ampacity = 33.25A
Conductor Size = 10 AWG, rated 30A at 60°C, 110.14(C)(1)(a)(2) and Table 310.16
What I don’t get is why is the conductor a parity above the ampacity of 10 awg? I thought the ampacity always had to be bigger than the calculated amps. Thanks for your time and knowledge!