Junction Box Labelling
kody916
Illinois
Hello Everyone,
when there are multiple voltages (120VAC & 24VC) present inside the same junction box, which NEC rule dictates the labelling the junction Box? i remember vaguely that a label needs to be put on the junction box which states "multiple voltage sources present" or something like that. but cant remember exactly. any suggestions?
Thank You
First off 120V and 24V can't be in the same junction box. That's the only NEC rule I know.
Sure they can, just needs to be a barrier between the compartments of the junction box.
AS for the labeling of the box, I don't think the NEC has anything to say about 120 V and 24 V.
-Hal
I think we have to more specific. If that 24v is class 2, I agree, but there is no general restriction that certain voltages be isolated.
How do RIBs get away with it?
Simple, IMHO. They are devices, not field wired boxes. A better question is how you stay compliant when you connect to those wires. if the low voltage coil circuit is classified and wired as Class 1 (Chapter 3 methods) it is much easier to comply!