Re: Junction Box Question
The removal of the guts of the panel is what generally creates the situation that is most quickly and economically fixed with a few tek screws.
The removal of the guts leaves an opening in the cover that has to be closed in some manner, 2005 408.7 (although one might argue that 408.7 doesn't specifically list "fuses", and therefore, that it doesn't apply).
In my jurisdiction, one can fashion a filler plate for the old fuse center OCPD opening, but it is a custom fabrication that takes time. Screwing down the panel cover door (the door hinged to the cover that gave access to the fuses) is an "approved means."
The old black painted steel panels, that usually only had 30 Amp services in them, and that had covers (hinged to the panel itself) that were one solid unbroken sheet of steel, are acceptable as is with only the original latch securing the cover in place.
There are also a whole raft of mid 20th century fuse centers that had a removeable dead front placed over the OCPDs which was, in turn, closed behind a hinged panel cover made of one unbroken sheet of steel. After removal of the dead front and the OCPD guts, the hinged cover is acceptable (again, in my jurisdiction of MN) as is without additional screws.