Are my calculating the minimum size required correctly per NEC 314.28(2)?
I have a pullbox with a 4 inch conduit entering and a 4" conduit exiting at the opposite wall (straight line). There is also a 1 inch conduit entering the bottom. So the 1" conduit is perpendicular to the 4" conduits. There is a splice within the box.
The length needs to be 6x4"=24"
The width needs to be 6X1"=6"
The depth doesn't have any requirement
Hoffman a reputable manufacturer has a standard size of 24"x6"x4.5" however I don't think a 4.5" depth is suitable given a 4" conduit is being used.
So I'm going to specify the minimum box size required is 24"x6"x6" which will need to be custom made.
I have a pullbox with a 4 inch conduit entering and a 4" conduit exiting at the opposite wall (straight line). There is also a 1 inch conduit entering the bottom. So the 1" conduit is perpendicular to the 4" conduits. There is a splice within the box.
The length needs to be 6x4"=24"
The width needs to be 6X1"=6"
The depth doesn't have any requirement
Hoffman a reputable manufacturer has a standard size of 24"x6"x4.5" however I don't think a 4.5" depth is suitable given a 4" conduit is being used.
So I'm going to specify the minimum box size required is 24"x6"x6" which will need to be custom made.