How would I size a JB to house two 2" conduits entering the same side of the box. The conductors will be H taped together.
Need more info.
Are there other conduits that the conductors enter or do they loop between these two ?
(U Pull, Angle pull or straight thru ??)
This may help
IMHO the C distance only applies to a continuous run of conductor in the first place.I have always found this distance C dimension to be silly when you're splicing the conductors together with something like a multi-port, Polaris style connector. IMO it's better if the conduit are right next to each other.
IMHO the C distance only applies to a continuous run of conductor in the first place.
So an attempt to apply it to a spliced or terminated conductor would indeed be silly.
Common sense and same Code reference. There's no straight, angle, or 'u' pull involved. The conductors are spliced, i.e. two conductors electrically coupled. Thus the conduit entries do not house the same conductor (which is the C dimension in the graphic).Code reference?
Code reference?
According to the title, logic says a splice cannot be an angle or u pull and thus spliced conductors cannot be the same conductor.Your graphic did say "enclosing the same conductor". Is a conductor still the same conductor, after it is spliced to another segment?
(2) Angle or U Pulls, or Splices.
The A dimension applies, the C does not.So then The graphic that Dennis posted does not apply to the OP?
The A dimension applies, the C does not.
I'm not... and I hope no inspector does....unless you want to call the spliced conductors the same conductor.
IMHO the C distance only applies to a continuous run of conductor in the first place.
So an attempt to apply it to a spliced or terminated conductor would indeed be silly.
Sent from my XT1585 using Tapatalk
I'm not... and I hope no inspector does.
That gives minimum distance between centerlines of field made entries, not NEC minimum distance required distances between entries in a pull box.