Junction box size

Status
Not open for further replies.

PWRUP

Member
How would I size a JB to house two 2" conduits entering the same side of the box. The conductors will be H taped together.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Need more info.
Are there other conduits that the conductors enter or do they loop between these two ?
(U Pull, Angle pull or straight thru ??)
 
Last edited:

PWRUP

Member
Need more info.
Are there other conduits that the conductors enter or do they loop between these two ?
(U Pull, Angle pull or straight thru ??)

No other conductors. Feeders will enter the same side of the box and will be spliced once.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
This may help

ry%3D400
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This may help

ry%3D400

I have always found this distance C dimension to be silly when you're splicing the conductors together with something like a multi-port, Polaris style connector. IMO it's better if the conduit are right next to each other.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I have always found this distance C dimension to be silly when you're splicing the conductors together with something like a multi-port, Polaris style connector. IMO it's better if the conduit are right next to each other.
IMHO the C distance only applies to a continuous run of conductor in the first place.
So an attempt to apply it to a spliced or terminated conductor would indeed be silly.

Sent from my XT1585 using Tapatalk
 

Smart $

Esteemed Member
Location
Ohio
Code reference?
Common sense and same Code reference. There's no straight, angle, or 'u' pull involved. The conductors are spliced, i.e. two conductors electrically coupled. Thus the conduit entries do not house the same conductor (which is the C dimension in the graphic).
 

Smart $

Esteemed Member
Location
Ohio
Your graphic did say "enclosing the same conductor". Is a conductor still the same conductor, after it is spliced to another segment?
According to the title, logic says a splice cannot be an angle or u pull and thus spliced conductors cannot be the same conductor.
(2) Angle or U Pulls, or Splices.
 

PWRUP

Member
IMHO the C distance only applies to a continuous run of conductor in the first place.
So an attempt to apply it to a spliced or terminated conductor would indeed be silly.

Sent from my XT1585 using Tapatalk

This is why I'm asking. My intention is to 'H' Tap the conductors together so putting the conduits closer together would make the installation easier and neater.
But reading the NEC makes me think it would need to be distance 'C'.
 

kwired

Electron manager
Location
NE Nebraska
I'm not... and I hope no inspector does. :D

Same here. Same scenario, but land conductors on a breaker - you often have lesser dimensions on the cabinet then is required for a box containing a U-pull.

Seen many 200 amp breaker enclosures that have line and load raceways leave the bottom that are only about 9 or 10 inches wide.

When the breaker is closed electrically the load side conductor is effectively an extension of the line side conductor, but they are still separate conductor segments that connect to the breaker, splicing device, etc. where a u-pull is hard to say there is more then one conductor (per ungrounded, grounded, line anyway).
 

kwired

Electron manager
Location
NE Nebraska