P Purr24 Member Location Pennsylvania Occupation Electrician Jul 22, 2021 #1 Are these support clips legal for small junction boxesAre these legal to support 1900 boxes?
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jul 22, 2021 #2 Yes, provided the support means meets the requirements in 300.11
roger Moderator Staff member Location Fl Occupation Retired Electrician Jul 22, 2021 #3 Yes, it is also specifically designed for that. From Caddy's website.
P Purr24 Member Location Pennsylvania Occupation Electrician Jul 22, 2021 #4 Thanks Sent from my Pixel 2 XL using Tapatalk
P Purr24 Member Location Pennsylvania Occupation Electrician Jul 22, 2021 #5 augie47 said: Yes, provided the support means meets the requirements in 300.11 Click to expand... Thanks I am using my own ceiling wire that is only supporting the box. Sent from my Pixel 2 XL using Tapatalk
augie47 said: Yes, provided the support means meets the requirements in 300.11 Click to expand... Thanks I am using my own ceiling wire that is only supporting the box. Sent from my Pixel 2 XL using Tapatalk
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jul 22, 2021 #6 I cringe when I see a number of those in a ceiling along with EMT (vs flex or MC). So often, on existing installs, the joints have uncoupled. I know the "it wasn't installed correctly" input but regardless it is too commonplace.