What is the limit in the amount of a "conduit run" before a junction box is required??
Thanks... Can't seem to find it.
Thanks... Can't seem to find it.
What is the limit in the amount of a "conduit run" before a junction box is required??
Thanks... Can't seem to find it.
As Dave says: The Code is silent about conduit run length between pull points.Thanks. For some reason I was thinking 100 ft. No wonder I couldn't find it
Technically, 24,901 miles. That's the circumference of the earth. One trip around would equal 360 degrees of bend.
Have fun pulling wire in.
Technically, 24,901 miles. That's the circumference of the earth. One trip around would equal 360 degrees of bend.
Have fun pulling wire in.
Technically, 24,901 miles. That's the circumference of the earth. One trip around would equal 360 degrees of bend.
Have fun pulling wire in.
You may well have been within hearing of someone saying, or "teaching", that. However, there is no Code citation that will limit the distance, and there IS a Code limit of 360 degrees of bend.I vaguely recall a rule of thumb of 40 ft and larger bend radii are considered "gentle" enough to not count in the 360 degree rule. Is this just my imagination?