I have a friendly bet going on with another PE...
Case: Metallic box has two metallic conduits coming into it. 120VAC power (one current carrying and one grounded) is routed through box continuously, no splices. A grounding conductor is routed through each conduit and comes into box and is connected to the other grounding conductor with a wire nut.
I say that the box needs to be bonded.
He says the box need not be bonded because its already bonded via conduit. I agree, but I think the code requires a bonding jumper...I just can't find it.
If this box was abandoned (and not connected) equipment, lets say a disconnect ... would that change anything?
Thanks,
Jason
Case: Metallic box has two metallic conduits coming into it. 120VAC power (one current carrying and one grounded) is routed through box continuously, no splices. A grounding conductor is routed through each conduit and comes into box and is connected to the other grounding conductor with a wire nut.
I say that the box needs to be bonded.
He says the box need not be bonded because its already bonded via conduit. I agree, but I think the code requires a bonding jumper...I just can't find it.
If this box was abandoned (and not connected) equipment, lets say a disconnect ... would that change anything?