Junction wires in a Trough

Status
Not open for further replies.

spencercagen

Member
Location
New jersey
Occupation
Electrician
How many 4/0 THHN can I fix in a 12x12x48 trough? What is the calculation for the trade size? This is going to be for a single family Mother/Daughter. 400 Amp single phase, 2 meter/Disconnects. Getting spliced in the trough. Is this allowed
 
The limit is 40% fill in cross-section area; you'll never get near it.

Yes, splicing is permitted.
 
If you are using power distribution blocks for the splices take a look at 376.56(B)(1) if you are under the 2017 or 2020 codes.
 