I am about to hire an Electrician to do some work for me and something just doesnt seem right.
Let me see if I can explain properly:
I have a manufactured home with an outdoor 200amp service panel. It feeds another 200amp service panel inside the home. It also feeds my work shop to a 100amp sub panel.
What I am doing is building a deck approx. 300' away from the work shop near the river. I want to have at least 4 circuits there for outdoor plugs, lights etc... So, I called an Electrician and here is his scope of work:
Run #8 AWG from the 100amp panel at the work shop to the deck location (300') in 1 1/2" schedule 40 PVC to feed another 100amp sub panel. From the new 100amp sub panel feed the 4 circuits of outdoor duplexes. To feed the duplexes he proposed to use direct burial romex cable and staple it to the deck posts.
I just want to check on here to see if all this sounds good and more importantly by code. The problem I have is feeding a 100 amp subpanel with another 100 amp subpanel...that just doesnt sound right and also why do I need another 100amp service panel if all I want is 4 circuits that will most likely never have a load on them at the same time. And the distance of 300', I would have thought would require a bigger wire size. and does it not need to be in rigid conduit? or is the schedule 40 ok. Also, not sure about stapling the wire to the deck posts...cant you attach conduit to the duplex gang boxes.
Any help would be great...thanks
Let me see if I can explain properly:
I have a manufactured home with an outdoor 200amp service panel. It feeds another 200amp service panel inside the home. It also feeds my work shop to a 100amp sub panel.
What I am doing is building a deck approx. 300' away from the work shop near the river. I want to have at least 4 circuits there for outdoor plugs, lights etc... So, I called an Electrician and here is his scope of work:
Run #8 AWG from the 100amp panel at the work shop to the deck location (300') in 1 1/2" schedule 40 PVC to feed another 100amp sub panel. From the new 100amp sub panel feed the 4 circuits of outdoor duplexes. To feed the duplexes he proposed to use direct burial romex cable and staple it to the deck posts.
I just want to check on here to see if all this sounds good and more importantly by code. The problem I have is feeding a 100 amp subpanel with another 100 amp subpanel...that just doesnt sound right and also why do I need another 100amp service panel if all I want is 4 circuits that will most likely never have a load on them at the same time. And the distance of 300', I would have thought would require a bigger wire size. and does it not need to be in rigid conduit? or is the schedule 40 ok. Also, not sure about stapling the wire to the deck posts...cant you attach conduit to the duplex gang boxes.
Any help would be great...thanks