Hypothetically, there is a piece of equipment protected with a fusible disconnect nearby with 30 amp fuses in it. This is fed from a panel with a 30 amp breaker.
This piece of equipment is replaced with a smaller one calling for a MOCP of 25 amps. A new 25 amp breaker is installed in the panel
Question is, is it ok to leave the 30 amp fuses in the fusible disconnect??
I'm aware it would be easier to just put 25 amp fuses in the disconnect but I'm curious if there is anything wrong with leaving the 30's in?