Member
The house is a two story there are two meters on the back of the house one meter feeds a panel in the garage which supplies the downstairs one meter feeds the panel on the 2nd floor which supplies the upstairs. the homeowner would like too upgrade his service too 200A and change both panels. the downstairs panel would be moved outdoors next too the meters (space permitting)
the upstairs panel wouls be replaced. Both panels would be fused at 100A.

service cables- from the meter base terminating in the panel box. I can run the cable on the exterior of the house. and I am going too have a blast running the groung and the cold water ground on the outside of the house down the side of a two story! any suggestions
 
Re: just curiouse?

Sorry for the confusing post I was tired! my question is can I fuse # 2al seu at 100A or should I buy copper (I hope not) any info is appreciated. Thanks
 
Re: just curiouse?

Read all of 310.15(B)(6) (not just the table) and I think you will find your answer.

Roger

[ March 17, 2004, 04:29 PM: Message edited by: roger ]
 
Re: just curiouse?

the meter bases will be located on the back exterior wall of the house the 100a panel that supplys the downstairs will be located next to or below the meterbases. The panel supplying the upstairs will be located on the 2nd floor with the service cable on the ouytside of the house and that panel may just be fused at 90A so that I can use #2AL SEU cable! :D
 