I have just perused UL943 that was issued back in 2006.
 
Ground fault circuit interrupters now actually check for ground faults.
 
GFCIs must trip if there is a neutral-ground on the load side of the GFCI. The UL standard for tripping on a N-G fault is the same as for a "normal" fault: T (trip time in seconds) = (20/mA)^1.43. There is no requirement that this N-G sensing be performed without some amount of current flowing and any current that may flow can be as high as 6mA.
 
But regardless of this new requirement the basic way a GFCI works remains the same: The current flowing out of the GFCI must not be more than 6mA different than the amount flowing back in.
 
edit: title change
	
		
			
		
		
	
				
			Ground fault circuit interrupters now actually check for ground faults.
GFCIs must trip if there is a neutral-ground on the load side of the GFCI. The UL standard for tripping on a N-G fault is the same as for a "normal" fault: T (trip time in seconds) = (20/mA)^1.43. There is no requirement that this N-G sensing be performed without some amount of current flowing and any current that may flow can be as high as 6mA.
But regardless of this new requirement the basic way a GFCI works remains the same: The current flowing out of the GFCI must not be more than 6mA different than the amount flowing back in.
edit: title change
			