I'm having an issue with the shop. I have a system designed as 208y/120. Now POCO is giving me 120/240 delta. (another long story) All the gear is mounted and has main breakers. Time to start shopping wire.
Soooo, the owner of our company says he will size the high leg 2 sizes smaller than the other ungrounded conductors. I say you cant do that the gear has main breakers. He tells me that won't make a difference since the high leg has higher voltage therefore smaller wire will carry higher amperage.
???

I continue that if you want to use a smaller high leg you calculate the load on it and fuse accordingly. I am told you are allowed 2 sizes smaller even with a breaker, and another guy at the shop agrees with him.
So I'm banging my head here looking for the article/section that allows this.
I know I'm right but a little brain dead tonight. Little help please.