I will certainly have to create some sort of low impedance path back to the source and hope that the ancient Trumbull OCPD with trip on a fault condition. I am just concerned with the shock hazard associated with this type situation. I don't want anyone to walk by and grab the railing or metal pipe and be electrocuted.
down the unit, sprinkle these at contact points.....
connect them with an unbroken bare #6 copper, leaving the tail end of
the ground wire long enough to hang down into the water, run it outside
of the conduit, exposed until it gets back up to something that is grounded
well, like a disconnect or box where you get from sealtight to hard pipe,
use a ground strap on that conduit, and turn it all back on.
nobody will go home dead. it'll work, and cost less than $100, including
labor.
if your employer balks at spending $100 on this, smile, nod, and go back
to looking on monster.com or craigslist for a new position.