But here goes... Isn't it 1000 because they are asking for maximum standard overcurrent device rating? next higher. This is the reason I was asking the question to begin with. Just wanting to check myself....


How did you come up with 1000?
 

joebell

Senior Member
Location
New Hampshire
But here goes... Isn't it 1000 because they are asking for maximum standard overcurrent device rating? next higher. This is the reason I was asking the question to begin with. Just wanting to check myself....

No the next higher does not apply as I posted earlier 240.4 (C) applies. If you have your code book I reccommend you reading 240.4 (C). You are dealing with an OCPD greater than 800 amps.
 