danilo

Member
Guys,

supposed in my computation for getting the k factor of transformer i got k=4. what would be its possible effect in the system if i use k=13 rated transformer instead?

Gracias!

Danilo
 
Re: K-Rated Transformer

It will work fine. You will get more core steel, a larger grounded conductor, and a higher cost but the transformer will work just fine. :D
 
Re: K-Rated Transformer

The K-Rating is a measure of the transformer's ability to tolerate the heat generated by the harmonic currents. You would simply be using a transformer that can tolerate more abuse that it is likely to see. It would be a bit of overkill, with a corresponding overcost, as Charlie said. But it gains you nothing in terms of extra capacity for adding load, and the distribution system will not notice the difference.

Danada.
 
Re: K-Rated Transformer

Three downsides of using a larger K rating than needed are that:
some manufacturers design the xfmr with a reduced impedance (from standard)
have higher inrush (since they sometimes use a somewhat standard large transformer and derate it) than you might expect for the nameplate size
and are physically larger than a typical xfmr or smaller k rating.
 