I have a temporary 1000 kVA "medium volt" transformer (25K/480/277) that is feeding a new construction job site. It has an impedance rating of 3.81% and according to the EOR he has based the calculated fault current at 31,570 amps assuming an infinite buss. The transformer feeds a 1200 amp disconnect that is fused at 700 amps supplying an 800 amp, 3-phase 480/277 volt panel used for the temporary on a new building under construction.
The problem is the 800 amp temp panel that was installed has a 14kaic rating and according to the Engineer it needs to be a 42kaic rated panel to handle the 31,570 fault current. I was somewhat surprised to see an available fault current study done on a temporary installation, but I see new stuff everyday.
My question is... can the 1200 amp disconnect be fused properly to protect the 800 amp panel with the 14kaic rating? Or does the panel need to be swapped out for one that is rated at 42kaic? How far down the line does this rating go (kaic)? We also have construction trailer that has a 100 amp panel inside the trailer that I am certain doesn't have a kaic rating that high that is being fed from a step down transformer coming out of the 800 amp temporary construction panel. How does the kaic rating affect that panel?
The problem is the 800 amp temp panel that was installed has a 14kaic rating and according to the Engineer it needs to be a 42kaic rated panel to handle the 31,570 fault current. I was somewhat surprised to see an available fault current study done on a temporary installation, but I see new stuff everyday.
My question is... can the 1200 amp disconnect be fused properly to protect the 800 amp panel with the 14kaic rating? Or does the panel need to be swapped out for one that is rated at 42kaic? How far down the line does this rating go (kaic)? We also have construction trailer that has a 100 amp panel inside the trailer that I am certain doesn't have a kaic rating that high that is being fed from a step down transformer coming out of the 800 amp temporary construction panel. How does the kaic rating affect that panel?