KAIC rating on a transformer

Status
Not open for further replies.

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
Just a bit of summarizing of other posts.

To answer your original question: It _may_ be possible to put a suitable fuse into your disconnect to properly protect the existing 800A panel. This is what is known as a 'series rating', and cannot be calculated, you need the manufacturer's blessing.

As others note, in their experience the series rating starts with a panel that has a 22 KAIC rating and the series rating goes up from there, meaning you may be out of luck with your 14KAIC panel.

As Jraef notes, during a fault motors can suddenly act as generators and feed energy into the fault. So if you want to use a series rating there is a rather strict limit on the total motor load connected to you system.

Electric-Light brings up an important point. The 'infinite buss' calculation is a quick and easy calculation to do, but it gives you a worst case result. The 'infinite buss' assumes that there is no restriction to current flow on the primary side of the transformer, and give you the fault current right at the transformer terminals.

But in the real world there will be some impedance in the MV lines feeding the transformer, some impedance at the substation feeding those lines, and some impedance in the wires from the transformer terminals to the panel. Prior to jumping through any other hoops, a more accurate calculation _may_ be in order.

This is not a no-brainer, however; depending on the location it may be quite difficult/expensive to get the primary fault current information. On the other hand, if you have 500 feet between the transformer/fuses and the panel, your secondary conductors may be sufficient to limit fault current.

-Jon
 
As others note, in their experience the series rating starts with a panel that has a 22 KAIC rating and the series rating goes up from there, meaning you may be out of luck with your 14KAIC panel.

I have one other comment: I assumed there was a MB in the panelbaord, which in my experience are usually at least 22KAIC. Upon rereading the OP, there is no specific indication that there is a MB, but it it seems that there should be, or be 6 or less breakers in the panelboard.
 

kwired

Electron manager
Location
NE Nebraska
This is not a no-brainer, however; depending on the location it may be quite difficult/expensive to get the primary fault current information. On the other hand, if you have 500 feet between the transformer/fuses and the panel, your secondary conductors may be sufficient to limit fault current.

-Jon
500 feet of conductor for under 1000 volts is probably plenty of length to limit fault current in most situations to at least 22kA or less, unless they are extremely oversized for the load/voltage drop considerations.
 

kwired

Electron manager
Location
NE Nebraska
The GFP issue still seems to a be a deal breaker though no?
I don't think OP has mentioned any distances for anything - which does impact available fault current at any particular point in the system, but yes GFP would be required for his application even if the available fault current were only 2000 amps.
 

dkidd

Senior Member
Location
here
Occupation
PE
I have one other comment: I assumed there was a MB in the panelbaord, which in my experience are usually at least 22KAIC. Upon rereading the OP, there is no specific indication that there is a MB, but it it seems that there should be, or be 6 or less breakers in the panelboard.

The fused switch protects the panel.
 