pgordon

Senior Member
Location
Maine
Occupation
Electrician
I am in need of some tech support.

I have one 600 amp (MDP) main distribution panel , main breaker 22 kaic

I have seven 100 amp sub panels in the field, main lug also rated 22 kaic

I have all the branch circuits breakers rated at 22 kaic.

My question is how the kaic ratings works here.

This is how I understand kaic ratings work .(please correct me)

Main panel main breaker 22kaic

Sub panel and all branch circuit breakers should be 10 kaic.

My thinking is that a 1 pole 20a,10kaic breaker would trip before the main breaker 22kaic would.

Any enlightenment would be great. PG


Also, what would be a series rated panel ?
Does this terminolgy change things?
 

ron

Senior Member
The AIC rating has essentially nothing to do with what trips first.
The AIC rating is the ability for the circuit breaker to interrupt a short circuit without blowing up. It is related to the calculated short circuit current at the bard base don the source fault current.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Basically you have two systems to think about. Fully rated systems would have every breaker rated at or above the available fault current. "series rated" systems are where systems have been tested and rated where the combination of breakers meets the fault current requirement.
You can not assume "series ratings". They must be listed by the manufacturer. All breakers won't series rate and series ratings don't cross manufacturers.
If you are depending solely on ratings to meet requirements and your system rating is "x" then you would need to check any breaker rated below "x" to assure it "series rates".
For example, a two pole 100 amp breaker might not series rate with your main where a 3 pole 20 might.
 
Last edited:

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
As Ron pointed out, the AIC rating has nothing to do with how fast a device trips.

As Gus said, a series rating is where two devices with different AIC ratings have been tested together.

What you have is a fully rated 22K AIC system.
What you are asking about is a series rated 22/10K AIC combination.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
... Sub panel and all branch circuit breakers should be 10 kaic.
The part where you went wrong is in the should be issue. It can be, which would make the down stream 10kAIC panels less expensive, but only if series tested together as mentioned above. Having them all rated for 22kAIC is a better choice if the AFC is above 10kA.
 
I do not know who's gear you are using but whoever they are, they should be able to help you with the series rating.

Makes me wonder if the engineer provided any point to point calculations on the one-line regarding aic. Seems odd to me that the aic would not be knocked down just by virtue of the feeder length from the MDP to the panels.
 

skeshesh

Senior Member
Location
Los Angeles, Ca
The AIC rating depends on many factors and should be calculated by an engineer. Just because an item is a subpanel does not necessarily mean it should rated less than the main distribution, although it could be. The earlier comments were all spot on. Below find a decent list of series rated items:

SqD: http://www.cooperbussmann.com/pdf/1572c3b7-882c-4bdc-b520-0ff0123439a5..pdf

GE: http://www.bussmann.com/library/techspec/Ge.pdf

Cutler-Hammer: http://www.cooperbussmann.com/pdf/c3c99bcd-e9fd-4521-b2d4-97fd1b2c4102..pdf

Disclaimer: make sure to check the series rating with the mfg. before installing anything. Series ratings can make your life much easier, but also much more difficult if something gets messed up and you didn't check the specification!
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
The AIC rating depends on many factors and should be calculated by an engineer. Just because an item is a subpanel does not necessarily mean it should rated less than the main distribution, although it could be. The earlier comments were all spot on. Below find a decent list of series rated items:

SqD: http://www.cooperbussmann.com/pdf/1572c3b7-882c-4bdc-b520-0ff0123439a5..pdf

GE: http://www.bussmann.com/library/techspec/Ge.pdf

Cutler-Hammer: http://www.cooperbussmann.com/pdf/c3c99bcd-e9fd-4521-b2d4-97fd1b2c4102..pdf

Disclaimer: make sure to check the series rating with the mfg. before installing anything. Series ratings can make your life much easier, but also much more difficult if something gets messed up and you didn't check the specification!

And to reiterate, if this all seems too complex just go with the same rating all the way through.
 
And to reiterate, if this all seems too complex just go with the same rating all the way through.

And just to reiterate your supplier and who he uses for gear can help with series rating.......... Could save a bunch if you can lower required aic.
 