Katt 2 speed 3 phase single winding 2/4 poles with 12 leads.

Status
Not open for further replies.
Take a pic of the data plate and post it here.
I dont have plate with me. its at the shop. very small data plate . not much to go on.
If you can't post a picture, try to post model number and as much other info as you can
plate is at shop. what i know is its a 160L frame.. lists 12.5/ 16 KW. 4/2. 400 volts +/- 10% 50hz
Y/D/Y/YY. i dont remember the amps or exact 50 hz rpm
 
Look at the bottom of this page.
are the leads labeled by chance?
2B08A5BE-75EB-4A30-B655-F1CDD6958C53.jpeg
 
all i can say is what ever this motor hooks up to must be a nightmare. I dont go out into the field work so im not any help there. the fella that pulled the motor said his customer was y- delta starting it. might explain the need for 12 leads. a bad bearing destroyed the winding. i have the new coils in.
 
Status
Not open for further replies.
Top