Just reading the 2008 code. Looks like they TRIED to make it simple for the generators when it needs bonding or not. Well the only thing i see someone debating is the 'PERMANENLY INSTALLED GENERATORS' seeing how they didnt DEFINE 'premanently installed'. (I know it sounds simple but i know someone would argue about any definition, ie. 'depends on your definition of sex')
Lets see if i got it now, PLEASE correct me if im wrong, For simplicity we will call the grounded conductor the NEUTRAL. This is for a simple house/dwelling when the power goes out.
Seperately Derived System is basically just a SWITCHED NEUTRAL. So if the transfer switch , switches the neutral when the generator is on then you got to drive ground rods and you bond the FRAME of the generator to the ground rods (via a gec) but you do NOT connect the neutral and grounds together at the generator since in most cases they are bonded together at the panel (service disconnect). Am i correct??
A NONseperately Derived System is when the neutral is NOT switched AT THE TRANSFER SWITCH, so the generator neutral and the UITILITY neutral are bonded together (assuming you pull a neutral from the generator) but the equipment grounding conductor(ground) is attach to the frame of the generator and ran to the Panel and connected to the GROUND bus of the panel(service disconnect). NO GROUND rods are driven for the generator because you are useing the UTILITY grounds (for lightning etc). And that neutral at the UTILITY is used to clear a fault path(trip a breaker)
The size of the Equipment bonding jumper on the SUPPLY side of the generator will be based on table 250.66 So assuming you have little over 5kw generator with a 30 AMP breaker then you need a # 8 copper. Seeing when the generator is on the transfer switch (hot)conductors are the temporary SERVICE ENTRANCE conductors (assuming they are sized accordingly to feed a30 amp).
The size of the LOAD side of the equip. bonding jumper is in accordance with table 250.122. so a 30 amp ocp would need a #10 copper.
So have i got this correct now for the 2008 code?? OR NO. Thanks for the help.Always learning.
Lets see if i got it now, PLEASE correct me if im wrong, For simplicity we will call the grounded conductor the NEUTRAL. This is for a simple house/dwelling when the power goes out.
Seperately Derived System is basically just a SWITCHED NEUTRAL. So if the transfer switch , switches the neutral when the generator is on then you got to drive ground rods and you bond the FRAME of the generator to the ground rods (via a gec) but you do NOT connect the neutral and grounds together at the generator since in most cases they are bonded together at the panel (service disconnect). Am i correct??
A NONseperately Derived System is when the neutral is NOT switched AT THE TRANSFER SWITCH, so the generator neutral and the UITILITY neutral are bonded together (assuming you pull a neutral from the generator) but the equipment grounding conductor(ground) is attach to the frame of the generator and ran to the Panel and connected to the GROUND bus of the panel(service disconnect). NO GROUND rods are driven for the generator because you are useing the UTILITY grounds (for lightning etc). And that neutral at the UTILITY is used to clear a fault path(trip a breaker)
The size of the Equipment bonding jumper on the SUPPLY side of the generator will be based on table 250.66 So assuming you have little over 5kw generator with a 30 AMP breaker then you need a # 8 copper. Seeing when the generator is on the transfer switch (hot)conductors are the temporary SERVICE ENTRANCE conductors (assuming they are sized accordingly to feed a30 amp).
The size of the LOAD side of the equip. bonding jumper is in accordance with table 250.122. so a 30 amp ocp would need a #10 copper.
So have i got this correct now for the 2008 code?? OR NO. Thanks for the help.Always learning.