inspectorsparky
Member
- Location
- Mansfield,TX
I would like to get some feedback on an issue we have in our city. Thieves are stealing the exposed GEC's from services on strip centers. I am reseaching the following for a proposal: With power company approval;
Typical service consists of a pad mount transformer feeding a tap can. In the tap can there is a neutral bar and three phase bars. I propose the the UFER, building steel, cold water and any other supplimentary grounding conductors for the shell building bond together on the neutral bar of the tap can. A bonding jumper will come off of the building steel and bond the copper cold water. This eliminates exposed GEC's on the exterior. The electrical contractors that come in and build individual services for lease spaces will then build their service, and have a choice of supplimentary grounding such as primary being a bonding jumper off of building steel and a secondary off of copper cold water sized according to Table 250.66. The contractor will then bond the neutral for his service at the disconnect as usual.
Are there cons to this method of installation? I cannot find it in violation of the NEC, and I do not feel this setup would cause a parallell path to ground if all GEC's are sized accoding to Table 250.66.
Thoughts?
Typical service consists of a pad mount transformer feeding a tap can. In the tap can there is a neutral bar and three phase bars. I propose the the UFER, building steel, cold water and any other supplimentary grounding conductors for the shell building bond together on the neutral bar of the tap can. A bonding jumper will come off of the building steel and bond the copper cold water. This eliminates exposed GEC's on the exterior. The electrical contractors that come in and build individual services for lease spaces will then build their service, and have a choice of supplimentary grounding such as primary being a bonding jumper off of building steel and a secondary off of copper cold water sized according to Table 250.66. The contractor will then bond the neutral for his service at the disconnect as usual.
Are there cons to this method of installation? I cannot find it in violation of the NEC, and I do not feel this setup would cause a parallell path to ground if all GEC's are sized accoding to Table 250.66.
Thoughts?