jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
Okay so I totally agree that you should be allowed to do what you want. But I would have taken a different emphasis on the code argument. As Wayne said, this is covered by 705.12(D)(2)(1). And -(2). I would argue that 705.12(D)(2)(3) does not apply because that section is about 'busbars in panelboards.' The location of connection you have described is not a panelboard.
Important to note to the AHJ that in the 2016 CEC (2014 NEC), the 120% rule no longer applies broadly to any 'busbar or conductor'. The language that used to be found in 705.12(D)(2) of the previous code no longer exists. The 120% rule now only applies to 'busbars in panelboards.' In fact, you have described that there aren't even any 'busbars' of any kind, which is the title of that subsection. Thus the 120% rule does not apply, and your disagreement about multiple feeders is moot.
Important to note to the AHJ that in the 2016 CEC (2014 NEC), the 120% rule no longer applies broadly to any 'busbar or conductor'. The language that used to be found in 705.12(D)(2) of the previous code no longer exists. The 120% rule now only applies to 'busbars in panelboards.' In fact, you have described that there aren't even any 'busbars' of any kind, which is the title of that subsection. Thus the 120% rule does not apply, and your disagreement about multiple feeders is moot.