Finn12067

Member
Location
Oregon
Occupation
Nurse practitioner
I saw on their website that kilns over 48A should be hardwired. Although yours seems to be exactly 48A, according to you, it might be good if you have your electrician install a 60A fused disconnect and direct wire the kiln. Of course you would have to get permission from the mfg to prevent voiding your warranty.
 

Finn12067

Member
Location
Oregon
Occupation
Nurse practitioner
Again thank you all for your interest and expertise - it’s been super helpful and you’ve helped me to noodle through my next steps .
I will post back when I hear back from MEC (the national certifying agency.)
after a conference call w the electrician, the electrical inspector and town building head this am - they are standing on the 50 amp breaker . The electrician has offered to hardware the kiln at no additional charge - if I can get ok from l&l to honor the warranty in that case.
So that’s where it stands - hopefully l&l will play along .
it would appear that the customer is caught between many sets of code/ regulations - this is a grey area and from other posts even on this forum - the plug is becoming an issue for many customers and electricians . Based on a very superficial understanding of the issue I get why electricians would have an issue w putting it on a 60 amp breaker.
Wish me luck lol 🤞
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
i had a customer request a buck/boost transformer be installed to drop the voltage down to 208. They said the heating elements were expensive to replace, so the lower voltage extended the life of the elements. I wired one for my baby sister about seven years ago. At first she wanted a meter down at the building she put it in, but I convinced her to just run a feed off my meter down there (about 100’) since she was only going to use it twice a year. It still has never been used! LOL!
 

Finn12067

Member
Location
Oregon
Occupation
Nurse practitioner
i had a customer request a buck/boost transformer be installed to drop the voltage down to 208. They said the heating elements were expensive to replace, so the lower voltage extended the life of the elements. I wired one for my baby sister about seven years ago. At first she wanted a meter down at the building she put it in, but I convinced her to just run a feed off my meter down there (about 100’) since she was only going to use it twice a year. It still has never been used! LOL!
Too funny !
 

Meltric_South

Member
Location
Austin, TX
Occupation
Regional Sales Manager
the plug is becoming an issue for many customers and electricians . Based on a very superficial understanding of the issue I get why electricians would have an issue w putting it on a 60 amp breaker.

As was mentioned before you may have concerns from the manufacturer of voiding the warranty from modifying the equipment, and I know several people watching the board already know this, but I thought I would mention 60A plugs and receptacles exist.
 

kwired

Electron manager
Location
NE Nebraska
Did this unit come factor wired with the 50 amp cord/plug or did someone else put it on? Distributor maybe?

Instructions should indicate what the supply options are, particularly if there is more than just one option.

I have to agree with others in that this unit is not very likely to draw full rating for more than 3 hours. It will cycle on/off as needed to maintain temperature setting.
 

Finn12067

Member
Location
Oregon
Occupation
Nurse practitioner
As was mentioned before you may have concerns from the manufacturer of voiding the warranty from modifying the equipment, and I know several people watching the board already know this, but I thought I would mention 60A plugs and receptacles exist.
Thank you for pointing that out again - gives me another option if the manufacturer won’t stand by
The warranty
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
For what its worth, we discussed this about 6 years ago, with no good conclusion:

Looking forward to the justification for 50A receptacles on 60A circuits with 48A loads. It might be as simple as 'this is the way we've always done it' from a time when the practice was acceptable.

-Jon
 

Finn12067

Member
Location
Oregon
Occupation
Nurse practitioner
For what its worth, we discussed this about 6 years ago, with no good conclusion:

Looking forward to the justification for 50A receptacles on 60A circuits with 48A loads. It might be as simple as 'this is the way we've always done it' from a time when the practice was acceptable.

-Jon
I will let you know what I find out but I think you are right - I had a like previous kiln installed approx 10 yrs ago and when the breaker and receptacle were installed - no questions / issues came up
 

kwired

Electron manager
Location
NE Nebraska
For what its worth, we discussed this about 6 years ago, with no good conclusion:

Looking forward to the justification for 50A receptacles on 60A circuits with 48A loads. It might be as simple as 'this is the way we've always done it' from a time when the practice was acceptable.

-Jon
48 amp load that is non continuous can be on a 50 amp circuit, so it comes down to is this a continuous load or not. If it takes more then 3 hours to reach setpoint, then it should be considered a continuous load
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
48 amp load that is non continuous can be on a 50 amp circuit, so it comes down to is this a continuous load or not. If it takes more then 3 hours to reach setpoint, then it should be considered a continuous load

As I understand it: a 48A load that is non-continuous can be on a 50A circuit (50A breaker and wiring)
A continuous 48A load needs to be on a 60A circuit (60A breaker and wiring)

What the manufacturers instructions state for 48A kilns is a 60A circuit with 60A wiring and a 50A receptacle and plug, which seems a hybrid of the two allowed installations.

-Jon
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
48 amp load that is non continuous can be on a 50 amp circuit, so it comes down to is this a continuous load or not. If it takes more then 3 hours to reach setpoint, then it should be considered a continuous load
From what I have read and the fact that this is common, I would hazard to guess the load is not continuous.

I used to repair kilns of this size and never went to solve a problem that looked like an overload. Mostly elements and bricks.
 
From what I have read and the fact that this is common, I would hazard to guess the load is not continuous.

I used to repair kilns of this size and never went to solve a problem that looked like an overload. Mostly elements and bricks.
I'm also in the definitely not a continuous load camp. This is one of these cases where the manufacturer says something stupid - they should let the electrician worry about the circuit sizing and just focus on making kilns 😠
 