gar
Senior Member
- Location
- Ann Arbor, Michigan
- Occupation
- EE
080524-1622 EST
Charlie:
There are only three wires on the top of the pole and the transformer primary is bridged across two of the top wires. Neither of these is outwardly, on the outside of the transformer, connected to the secondary neutral. If one of the top wires is the neutral of a Y, then it must be jumpered inside the transformer. There is no secondary neutral running between poles and another transformer that could also be the primary neutral.
If the load was Y, then why bother to run 3 wires instead of just two?
Do you ever use a Y source at the substation and then only load it as delta and not carry the neutral with the distribution lines? One IEEE summary does seem to indicate this is used: "three-wire service, wye-delta". This was from
http://ieeexplore.ieee.org/Xplore/login.jsp?url=/iel2/820/3079/00095535.pdf?temp=x .
.
Charlie:
There are only three wires on the top of the pole and the transformer primary is bridged across two of the top wires. Neither of these is outwardly, on the outside of the transformer, connected to the secondary neutral. If one of the top wires is the neutral of a Y, then it must be jumpered inside the transformer. There is no secondary neutral running between poles and another transformer that could also be the primary neutral.
If the load was Y, then why bother to run 3 wires instead of just two?
Do you ever use a Y source at the substation and then only load it as delta and not carry the neutral with the distribution lines? One IEEE summary does seem to indicate this is used: "three-wire service, wye-delta". This was from
http://ieeexplore.ieee.org/Xplore/login.jsp?url=/iel2/820/3079/00095535.pdf?temp=x .
.