I've never seen a kitchen that had standby power. Is this a healthcare or nursing home facility?
The reason it's on standby power is that even though the normal power to the underhood lighting, receptacles and appliances is down (which the Ansul system would shut down anyway when triggered), in the event of a fire during the outage somebody wants the Ansul system to be operational as well as the exhaust fan.
-Hal
If you have stand-by power why not? It is a fire system, no?
-Hal
..even those systems that do use solenoid electric gas valves, the valves are powered open and will close on power failure. They will not reopen when power is restored without manually activating the relay reset..
Ahhh so, to avoid blowing $5000.- in Halon discharge, cleanup, & recharge, perhaps don't remove strange lock on red circuit breaker, nor open that fuse box disconnect, until we confirm Ansul system is mechanical with no solenoids?
Gadfly explained it better than I did. Apparently the engineer is considering these fire systems or part of the fire system. The Ansul system itself is mechanical and will function with or without power. Usually the exhaust fan is turned on or continues to operate when the Ansul system is triggered, but as noted, it isn't critical for the fire suppression.
-Hal
I don't know where you learned fire suppression technique.....
I don't know where you learned anything about Ansul systems but you need to go back and study again.
Re read my post. I'm referring to enabling the fan in the event of fire.
You are the one who needs to put your head in gear before your mouth.
Got that? Or do I have to hold your hand.
Re read post #10 as many times as you have to until it sinks in.Re read my post. I'm referring to enabling the fan in the event of fire.
You are the one who needs to put your head in gear before your mouth.
Not on a first date.Got that? Or do I have to hold your hand.
You need a little humility in your life, because you sure don't know much about kitchen suppression systems and their requirements. In many jurisdictions, it's required that the exhaust fan turn on or remain on in a hood fire. Functionally, the reason is to pull the fire back from the face of the hood, possibly creating a safer path for occupants to exit as well as limit any smoke condition in the kitchen. Most kitchens I have seen have prep tables directly in front of the cook line and your only path of egress may force you past the fire.
In my nine years with a contractor I designed and supervised the installation of over 100 kitchen suppression systems, not merely attended the occasional brush-up seminar.
The thread you linked to is about HVAC fans not kitchen exhaust hoods.....To answer your generalized treatment of exhaust fans in the event of fire, the link below will help you refine your knowledge:
http://www.eng-tips.com/viewthread.cfm?qid=119122
Ahhh so, to avoid blowing $5000.- in Halon discharge, cleanup, & recharge, perhaps don't remove strange lock on red circuit breaker, nor open that fuse box disconnect, until we confirm Ansul system is mechanical with no solenoids?
The idea of turning the fan on when there is fire is ridiculous. You'd be creating a blow torch if you did that..
..An Ansul system IS NOT a Halon system! Two completely different animals..
Can shutting off breakers discharge the Halon system?