spencert
Member
- Location
- California
- Occupation
- Homeowner/Engineer
Hey guys,
I'm an owner/builder with extensive electrical experience (father is retired industrial journeyman) in Southern California and I'm looking for feedback on the best way to handle a situation where I was failed on final due to GFCI receptacles not being installed even though dual function AFCI/GFCI breakers are present and were tested by the inspector to provide the required GFCI protection (they tripped). The inspector claims the "GFCI reset switch MUST be in the same room as the branch circuit protected" and that dual function AFCI/GFCI breakers don't meet the accessibility requirements. He referenced the definition for article 100 "readily accessible." I've appealed citing 422.6(B)1 that explicitly allows branch circuit overcurrent devices to provide the required GFCI protection and 240.24 that enforces that circuit breakers MUST be in a readily accessible location and my panels were previously inspected and approved by the AHJ therefore the breakers are readily accessible. The AHJ is still currently requiring installation of GFCI outlets in addition to the dual function AFCI/GFCI breakers installed the panels that have been proven to provide the required GFCI protection in the required locations. I should note that there are no published local amendments and the 2022 CEC has been adopted in its entirety.
I guess my question is more of a how to handle the situation. How can they simply ignore 422.6(B)? I believe that the 2022 California Electric Code explicitly allows the GFCI protection to come from the breaker, and there is no requirement that the reset switch "be in the same room" as the branch circuit. I've appealed, but per municipal code, I have to pay for a NFPA review. Should I just bite the bullet and pay to swap out breakers and install GFCI outlets to make the AHJ happy even though that in my opinion the current installation is code compliant and superior to GFCI receptacles? How would they handle a 240V branch circuit without a GFCI receptacle? I don't understand the argument. Safety has been proven on the branch circuit.
I understand the AHJ can "interpret" but this seems to be in black and white. Is there something I'm missing?
Thanks for your feedback!
I'm an owner/builder with extensive electrical experience (father is retired industrial journeyman) in Southern California and I'm looking for feedback on the best way to handle a situation where I was failed on final due to GFCI receptacles not being installed even though dual function AFCI/GFCI breakers are present and were tested by the inspector to provide the required GFCI protection (they tripped). The inspector claims the "GFCI reset switch MUST be in the same room as the branch circuit protected" and that dual function AFCI/GFCI breakers don't meet the accessibility requirements. He referenced the definition for article 100 "readily accessible." I've appealed citing 422.6(B)1 that explicitly allows branch circuit overcurrent devices to provide the required GFCI protection and 240.24 that enforces that circuit breakers MUST be in a readily accessible location and my panels were previously inspected and approved by the AHJ therefore the breakers are readily accessible. The AHJ is still currently requiring installation of GFCI outlets in addition to the dual function AFCI/GFCI breakers installed the panels that have been proven to provide the required GFCI protection in the required locations. I should note that there are no published local amendments and the 2022 CEC has been adopted in its entirety.
I guess my question is more of a how to handle the situation. How can they simply ignore 422.6(B)? I believe that the 2022 California Electric Code explicitly allows the GFCI protection to come from the breaker, and there is no requirement that the reset switch "be in the same room" as the branch circuit. I've appealed, but per municipal code, I have to pay for a NFPA review. Should I just bite the bullet and pay to swap out breakers and install GFCI outlets to make the AHJ happy even though that in my opinion the current installation is code compliant and superior to GFCI receptacles? How would they handle a 240V branch circuit without a GFCI receptacle? I don't understand the argument. Safety has been proven on the branch circuit.
I understand the AHJ can "interpret" but this seems to be in black and white. Is there something I'm missing?
Thanks for your feedback!