Kitchen Dishwasher and Disposal

Status
Not open for further replies.

Naga

Member
Location
Hawaii
Occupation
Electrician
Hi Guys,

Had a question. I am doing a job where the owner changed his kitchen cabinets and I had to take apart the disposal and dishwasher boxes and put new ones because the locations changed not more than a few feet. The inspector now says the disposal and dishwasher have to be Gfci only problem is I found out the circuits are being fed by a 12/3 mwbc so they are sharing the neutral. Can the dishwasher and disposal be considered grandfathered in so I don't need to make them GFCI or if they have to how do I make this work? Use a 20amp 2pole GFCI breaker?


Thanks,
Grant
 
I would use a dp gfci. I have never heard that ruling about a mwbc. Only the inspector can answer whether or not they will require gfci. IMO, if you messed with it then you have to bring it to code.
 
The inspector now says the disposal and dishwasher have to be Gfci only problem is I found out the circuits are being fed by a 12/3 mwbc so they are sharing the neutral
Not an issue if you use a 2-pole GFCI breaker.
 
Ok I can use a 2pole 20amp to make both circuits GFCI but if it has to be also AFCI what can I do? The Arc fault wont work on a shared neutral
 
Agree with @electrofelon make it one circuit. A DW usually can work on a 15 am circuit so a 20 will probably do the DW & the disposal
Yeah probably find most of the time, but You do have to be a bit careful, I got zinged for this once where the dish and disposal were both on the larger side and the math didn't work out. The solution was the HO got the next size smaller disposal, like 1/3 horsepower instead of 1/2 or whatever it was.
 
Status
Not open for further replies.
Top