2014 NEC in 210.8(D) to have GFCI protection the Kitchen Dishwasher Outlet.
Comment/questions
I don't see this restricted to dwelling units, am I correct on this?
What is there is no outlet - IE come out of wall with NM cable go straight to the DW? If no outlet does it require GFCI protection?
Dwelling units require AFCI protection for Kitchens, how can we get AFCI of the outlet and GFCI protection also?
210.8 (A) and (B) have 125 V single phase, 15 and 20 ampere receptacle language, 210.8(C) is for 240 volt outlets. It appears the intent was to protect the branch circuit but this may require a GFCI blank face receptacle feeding the dishwasher "outlet".