I'm confused by your marking the switches AFCI. I've never seen an AFCI switch, and the use of AFCI receptacles is restricted. Are you just indicating that the circuit is protected by an AFCI breaker? Your GFI markings are inconsistent as well. Note that the UC receptacle for the mixer in the island probably is close enough to the prep sink to require it to be GFCI protected as well.
If I understand your nomenclature, you have receptacles in the "enclosed porch" walls that share a circuit with the penninsula receptacles. This is not allowed.
Some notes that are distinct from code issues:
I like to put the receptacle for the dishwasher under the sink if you're using the plug as the service disconnect. It's a pain to have to completely pull out the dishwasher to disconnect it.
You show a gas range with a 30A receptacle. Is this a dual thing (gas cooktop/electric oven? Then that makes some sense. If it's all gas, you may need a smaller circuit to run the few electric gizmos (clock, igniters). If you're trying to future proof things, you may want to at least run the conductors for 50A, in case a future electric range is installed.
If I understand your nomenclature, you have receptacles in the "enclosed porch" walls that share a circuit with the penninsula receptacles. This is not allowed.
Some notes that are distinct from code issues:
I like to put the receptacle for the dishwasher under the sink if you're using the plug as the service disconnect. It's a pain to have to completely pull out the dishwasher to disconnect it.
You show a gas range with a 30A receptacle. Is this a dual thing (gas cooktop/electric oven? Then that makes some sense. If it's all gas, you may need a smaller circuit to run the few electric gizmos (clock, igniters). If you're trying to future proof things, you may want to at least run the conductors for 50A, in case a future electric range is installed.