Is it okay code-wise to have two gfci receptacles for a kitchen countertop on the same 20amp circuit? (NEC 2014, NYC)
Yet, I find them improperly connected all the time. It works, but the homeowner has to learn to reset them in the proper order.As charlie mentioned, you'll need at least one more SABC to feed a minimum of one more receptacle service the countertop.
Also, you would not line-load protect the 2nd GFCI off the first.
Yet, I find them improperly connected all the time. It works, but the homeowner has to learn to reset them in the proper order.
Connecting to line side terminals only would be wise when doing that. With newer GFCI's and use of the load side terminals, you still need to figure out which leads are line and which are load or you never will get it to reset.Some people install all GFI's on countertop just for cosmetics. They are confused about the proper wiring.