In a residence kitchen all counter top recp's are to be GFI protected but what about the refrigator recp. if it is next to the counter. Can it be a regular duplex receptacle?? If not do you have a code section.
 
Only receps that serve the c'top are required to be GFI-protected. 210.8(A)(6). If the recep is behind the fridge, 210.8(A)(6) does not apply.
 
210.8 Ground-Fault Circuit-Interrupter Protection for Personnel.

(A) Dwelling Units. All 125-volt, single-phase, 15- and
20-ampere receptacles installed in the locations specified in
(1) through (8) shall have ground-fault circuit-interrupter
protection for personnel.

(6) Kitchens ? where the receptacles are installed to serve
the countertop surfaces

Your recept is installed to serve the ref., not the countertop.
 
It's like Mary and Rhoda with all the echo's 480 :D

Better pick it up there, celt..... the old guy's beatin' ya up!

Typingman.jpg


giggle.gif
 
I know the original poster is talking about a kitchen but....

One thing to keep in mind is that if a receptacle for a refrigerator is installed within 6 feet of a wet bar sink then the receptacle must be GFCI protected.

I get alot of upset people when I tell them this as they are use to not GFCI protecting a refrigerator.