Not at all. If I put one receptacle within 3 feet of the bathroom sink, and a second receptacle 5 feet from the sink, have I met the requirement of, ?At least one receptacle within 3 feet?? Yes I have. On the other hand, if I put one receptacle 6 inches below an island countertop, and a second receptacle at toe kick level, have I met the requirement of, ?Receptacle outlets shall be located above . . . the countertop,? or at least have I met the exception, ?. . . receptacle outlets shall be permitted to be mounted not more than 12 inches below a countertop . . . ?? No, I have not.
The difference between the island and peninsula rule and all other receptacle rules is that it has a location requirement that begins with ?Receptacle outlets shall be located. . . .?