Re: Kitchen Island requirement...
Exception to (5): To comply with the conditions specified in (1) or (2), receptacle outlets shall be permitted to be mounted not more than 300 mm (12 in.) below the countertop. Receptacles mounted below a countertop in accordance with this exception shall not be located where the countertop extends more than 150 mm (6 in.) beyond its support base.
And I agree due to:Originally posted by LawnGuyLandSparky:
If there's no overhang, I'd say yes. If there IS an overhang (many penninsulas overhang to create a breakfast "bar," though I'm sure many eat other meals there as well) then I'd say no, because it's more of a built-in table or furniture.
Exception to (5): To comply with the conditions specified in (1) or (2), receptacle outlets shall be permitted to be mounted not more than 300 mm (12 in.) below the countertop. Receptacles mounted below a countertop in accordance with this exception shall not be located where the countertop extends more than 150 mm (6 in.) beyond its support base.