The NEC does not have a minimum distance. The maximum would be 2 feet from the appliance to the first receptacle, and 4 feet to each of the next ones. I would not want a receptacle closer than 2 feet from a stove or sink, but that is a design choice, not a code requirement.
Thanks for the help
I have a counter top next to both sides of range, which is 18" wide. But, it looks like I added way to many receptacles on the floor plan.
See attach Kitchen Layout for your reference.
Range shows one receptacle for the oven, the other one for the hood/microwave.
View attachment 22578
If you had three feet of counter between the range and the sink, you would be required to have at least one receptacle serving that counter. If you only have one it will be within 2 feet of one end or the other to comply.The NEC does not have a minimum distance. The maximum would be 2 feet from the appliance to the first receptacle, and 4 feet to each of the next ones. I would not want a receptacle closer than 2 feet from a stove or sink, but that is a design choice, not a code requirement.
Looks like you placed them about as minimal as code will allow to me.If I want to add a receptacle next to a range, sink or refrigerator does the distance from the edge of the appliance needs to be 1ft or 2ft away.
Since I'm getting conflicting results. Please see attach picture. Thanks
Looks like you placed them about as minimal as code will allow to me.
BTW 2017 NEC does not require the receptacle at the end of the peninsula if there is a receptacle at the "connected perpendicular wall"
....My next question, since you are required to a minimum of 2 Kitchen Receptacle, how many circuits can you connect to them or do they have to be dedicated circuits.