jimwalker
Senior Member
- Location
- TAMPA FLORIDA
Can a receptacle at a kitchen counter also cover wall space next to it.Meaning can i cover a wall spce within 6 feet of that receptacle on counter or does it require a seperate receptacle ?
Good CallOriginally posted by physis:
I'll get the popcorn.
Since the side of the cabinet at the end of the kitchen contitutes a "wall", then the wall space receptacle couldn't be behind that wall, could it?210.52(A)(2) Wall Space. As used in this section, a wall space shall include the following:
(3) The space afforded by fixed room dividers such as free-standing bar-type counters or railings
Just in it for the funsometimes I can be reckelss
Based on the findings in the 2005 cycle of the NEC I will say that as long as the receptacle is no higher than 5 ? ft from the floor and not part of a wall that is broken by doorways, fireplaces, and similar openings and not beyond the perimeters of such things such as freestanding bar-type counters or railings nor separated by rangetops, refrigerators, or sinks and are part of the circuits being installed with the appropriate section of the code then every thing is cool.210.52 Dwelling Unit Receptacle Outlets.
This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. Receptacle outlets required by this section shall be in addition to any receptacle that is part of a luminaire (lighting fixture) or appliance, located within cabinets or cupboards, or located more than 1.7 m (5? ft) above the floor.
(2) Wall Space. As used in this section, a wall space shall include the following:
(1) Any space 600 mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways, fireplaces, and similar openings
(2) The space occupied by fixed panels in exterior walls, excluding sliding panels
(3) The space afforded by fixed room dividers such as freestanding bar-type counters or railings
(4) Separate Spaces. Countertop spaces separated by rangetops, refrigerators, or sinks shall be considered as separate countertop spaces in applying the requirements of 210.52(C)(1), (C)(2), and (C)(3).
As pointed out above these circuits are allowed to be installed to cover all this area.(B) Small Appliances.
(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
"They" haven't spent much time in this forum.Originally posted by physis:
They say this one's too easy to make it very far.
Originally posted by electricmanscott:
"They" haven't spent much time in this forum. :roll:
Indeed this correct. The trouble is that you forgot to go back and look at 210.52(A)(1) again to see how it applies while keeping this in mind.By Charlie B.
I submit that you have to measure that six feet along the floor line.