Nope. The "2 minimum required circuits" are required to have no other outlets than receptacle outlets in a specific set of rooms. Reference 210.52(B) (1) and (B)(2).Sam65 said:Can a dishwasher be on the same circuit as the counter top receptacles if the 2 minimum required circuits are meet?
charlie b said:
Nope. The "2 minimum required circuits" are required to have no other outlets than receptacle outlets in a specific set of rooms. Reference 210.52(B) (1) and (B)(2).
Hey at least Charlie gave the guy a code reference to read. :grin:stickboy1375 said:They will never learn if you just give out the answers. :wink:
stickboy1375 said:They will never learn if you just give out the answers. :wink:
Sam65 said:Your able to put a fridge on sam circuit, why not a dishwasher?
Dennis Alwon said:Hey at least Charlie gave the guy a code reference to read. :grin:
Sam65 said:Your able to put a fridge on same circuit, why not a dishwasher?
maybe because refrigerator isn't fixed in place where as a dishwahser is? Or maybe since most dishwasher ( or at least all of the ones I've ever wired and seen) are hard-wired not plug-in type? Just guesses though.Sam65 said:Your able to put a fridge on sam circuit, why not a dishwasher?
steelersman said:maybe because rigrigerator isn't fixed in place where as a dishwahser is? Or maybe since most dishwasher ( or at least all of the ones I've ever wired and seen) are hard-wired not plug-in type? Just guesses though.
No you are not!Sam65 said:Your able to put a fridge on sam circuit, why not a dishwasher?
charlie b said:
No you are not!
You are allowed to put the fridge on an individual 15 amp circuit, or if you prefer on an individual 20 amp circuit. But that circuit is not a member of the "Small Appliance Circuit Club." What the Exception is taking exception to is the notion that all wall and floor receptacles are to be supplied with SA circuits. The Exception allows us to put that particular wall receptacle on a circuit that is not an SA circuit.
stickboy1375 said:Maybe they feel its a small appliance... :grin:
What year did that rule start? Cause I've always put fridge on SA circuit unless I knew it was gonna be a monster fridge like Viking or Sub-Zero.charlie b said:No you are not!
You are allowed to put the fridge on an individual 15 amp circuit, or if you prefer on an individual 20 amp circuit. But that circuit is not a member of the "Small Appliance Circuit Club." What the Exception is taking exception to is the notion that all wall and floor receptacles are to be supplied with SA circuits. The Exception allows us to put that particular wall receptacle on a circuit that is not an SA circuit.
Yes you can put a fridge on the same curcuitcharlie b said:
No you are not!
You are allowed to put the fridge on an individual 15 amp circuit, or if you prefer on an individual 20 amp circuit. But that circuit is not a member of the "Small Appliance Circuit Club." What the Exception is taking exception to is the notion that all wall and floor receptacles are to be supplied with SA circuits. The Exception allows us to put that particular wall receptacle on a circuit that is not an SA circuit.
Mea culpa, mea culpa, mea maxima culpa.stickboy1375 said:Yes, you are... :grin: Might wanna reread that section Charlie.
charlie b said:
Mea culpa, mea culpa, mea maxima culpa.
I was focusing on the exception, and forgot to read the rule itself.