Ok im fine with 210.52c if i had a counter top.
Now if there is no counter top at all,then 210.52c does not apply.Right ?
What im looking for is something to say that i need more than 1 SA circuit to cover the walls.
What it says is the 2 or more SA circuits required by 210.11 c 1 shall serve the receptacles covered by 210.52a and c
Going to 210.11 c 1 to see what it REQUIRED
It sends me back to 210.52 b to see what is SPECIFIED
We are now in a circle.Nothing has said so far that i need 2 SA circuits unless i have a counter top.
210.52 b 3 says the receptacles installed in a kitchen to serve COUNTERTOP SURFACES( we have none )shall be supplied by not fewer than two SA branch circuits,EITHER or BOTH of which shall also be PERMITTED to supply receptacles in the same kitchen and in other rooms specified in 210.52 b 1
Im reading this to say i can cover my kitchen walls with ONE SA circuit.It said i was permitted to use the 2 SA circuits serving counters, not that i had to use them.So since they were not required because there is no countertop to be served ,i am then allowed to run 1 SA circuit to take care off the walls.
Im sure this is not what they had in mind, and they never gave any thought to there being no countertop.
Follow this letter by letter and you will maybe understand.By no means am i saying i would do this,but then when is the last time you seen a counter less kitchen?
Can't put receptacles in to serve a counter less kitchen.
The article was just badly writen.