(Quote from seperate post of mine, yesterday)
"I searched "Knob..." on the archives. I was a bit discouraged, possibly abit confused by the information I found there. The Job that I am looking at has the typical new-to-old splicing nasties that I'm sure most of you have seen, plus some J-boxed work that, on the surface, looks pretty good, but I'm sure was unpermitted.
From what I could glean(sp) from the posts, it sounds like you can feed old K&T from new romex, but not the reverse? I don't want to get into soldering (especially in a hot attic), so J-boxing is the way to go, but the flying neutral-only, or hot-only splices need re-work, containment, and jumpers. It seems, from my reading, that there is no allowed single conductor or Romex usage for thse jumpers. Its a rule for me never to use old wire in repairs, due to unknowns, so it seems there is no repair option, for some of this work, just replacement. Have I read this right?"
TODAY
RE:394.10 (1).
"...knob and tube shall be permitted...as follows: (1) For circuit extensions of existing installations"
So for the purposes of the repair (to be inspected), using a NM box for the splices, with intregal clamps, and following the guidelines of the official NEC 2005 handbook, it would seem that THHN is an acceptable conductor (exposed/visible) as per the added note of explanation in the handbook, "Conductors used for knob and tube work may be of any general use type specified by Article 310."
This repair is needed to resolve mid-air flying splices (spider web splicing) in the attic. This is not truly an extension, as I think of an extension (as in adding another receptacle).
Does anyone see a conflict within the bounds of the code for this action?
TODAY
RE:394.10 (1).