Problem is we have instructors telling our agencies that you may not splice into K&T wiring and that you must run a home run from the panel, in order to do blow insulation in the attic. We always thought you could snip and tap from a junction box in the attic and continue from there? Need to find clear direction in the NEC to put this to rest..
250.130(C).
That is the section that will require you to usually fish to the basement. It won't disallow you from continuing to use the old K+T homeruns, but you have to properly bond the newly installed equipment grounding conductor in the NM.