I'm looking at some old K&T ...initially thinking the 14 AWG is over fused with a 20A fuse.
However, looking at Table 2, Chap. 10, 1953 NEC [house built in 1955] the ampacity for #14 is 20A...and note 3 to the table reads:
'For...concealed K&T work, the allowable current-carrying capacities of Table 2 shall be used.'
I can't find a code section similar to our current 240.4(D) for small conductors.
So? It's OK to use a 20A fuse with the old K&T 14 AWG wire?