mtnelectrical
- Essex, New Jersey
A GC has accidentally cut one Knob & Tube conductor, Is there a listed splicer to repair this?
coulter said:K & T may have still been around when I started, but I don't have any time on it. So, are the conductors generally stranded or generally solid? I thought they were solid.
carl
1793 said:I have never seen stranded, only solid
al hildenbrand said:The K&T solid is coated with tin and is, in my estimation, not quite as soft as contemporary NM-B solid conductors.
The main use of the tin is to isolate the copper from the natural rubber/synthetic rubber insulation. The copper is chemically affected by contact with the rubber.jes25 said:What was the purpose of tin coating?
tshea said:I would splice the wires together using a butt splice that is crimped in place and cover with heat shrink tubing. (Not necessarily in that order!)
dlhoule said:tshea said:I would splice the wires together using a butt splice that is crimped in place and cover with heat shrink tubing. (Not necessarily in that order!)
When you put the heat shrink on first, how do you make the splice?![]()