Rockwalker
Member
- Location
- Lihue, HI, USA
Recently I have been in a discussion regarding closing unused openings in junction boxes and the acceptable means or materials used for closing the openings. Some of the electricians on our project are under the impression that any unused openings in their junction boxes are considered effectively sealed/closed by the installation of the external fire pads and do not require an actual KO seal prior to the installation of the fire pad. Please see the attached photos for reference.
After reading through NEC article 110.12 (a) Unused Openings I found that this article states “Unused openings, other than those intended for the operation of equipment, those intended for mounting purposes, or those permitted as part of the design for listed equipment, shall be closed to afford protection substantially equivalent to the wall of the equipment. Where metallic plugs or plates are used with nonmetallic enclosures, they shall be recessed at least 6mm (1/4”) from the outer surface of the enclosure”. This does not specifically state that metal KO seals are required.
The underlined section “substantially equivalent to the wall of the equipment” is what seems to be the part that requires better definition. Article 100 Definitions does not cover this.
The question is, does the fire pad count as an acceptable means of closure? Technically it is approximately twice as thick as the wall of the 4S boxes that are being used.
After reading through NEC article 110.12 (a) Unused Openings I found that this article states “Unused openings, other than those intended for the operation of equipment, those intended for mounting purposes, or those permitted as part of the design for listed equipment, shall be closed to afford protection substantially equivalent to the wall of the equipment. Where metallic plugs or plates are used with nonmetallic enclosures, they shall be recessed at least 6mm (1/4”) from the outer surface of the enclosure”. This does not specifically state that metal KO seals are required.
The underlined section “substantially equivalent to the wall of the equipment” is what seems to be the part that requires better definition. Article 100 Definitions does not cover this.
The question is, does the fire pad count as an acceptable means of closure? Technically it is approximately twice as thick as the wall of the 4S boxes that are being used.